On est bien d'accord, vous n'avez rien compris !
25 fois le courant nominal !
Le courant nominal EST le courant de magnétisation, soit 25 milli-Ampères (MESURES à vide dans un transfo de 500 VA) et en régime établi!
Or, 25 fois 25 milliAmpères = 625 milliAmpères, le voilà, vôtre courant d'appel, bien inférieur à 166 Ampères !
Sig
Euh!! le courant nominal c'est pas celui la ...
Le courant nominal c'est celui qui correspond à la puissance nominale de ton transfo. soit 2 ou 3 ampère selon la puissance de ton transfo. et 10 à 20 x 3 A = 30 à 60 A .
Maintenant si tu veux réécrire les lois électromagnétiques, libre à toi, mais fais deja un simple recherche sur google et tu trouveras quelques milliers de sites qui parlent de ça:
citation d'un professeur d'université:
"A transformer switching onto a line can sometimes cause a circuit breaker to trip or a fuse to blow. This phenomenon occurs even if the transformer presents no load, such as when the secondary is open. The problem arises because of the heavy magnetizing inrush current in the transformer. The amplitude of the current depends on the instant on the ac waveform at which the transformer becomes energized. The inrush current is at its maximum value if the transformer becomes energized when the ac waveform goes through its zero-crossing point.
In this case, the inrush current is at its maximum when the ac waveform goes through its peak value. Normally, a mechanical contactor effects the switching without any control of the instant of switching. The inrush current dies down exponentially to the normal operating value of the load within a few cycles".
en substance pour les non anglophones ça dit que: Quand tu branches un transfo tu peux faire peter le fusible. Ce phenomène arrive même si le transfo n'a pas de charge, comme par exemple le secondaire ouvert. Ce problème est du aux courants d'appel de magnetisation.
L'amplitude de ce courant depend de l'instant du sinus sur lequel le transfo est "allumé"....
une autre citation d'une société qui fabrique des protections en courant de transfo :
"When an unloaded distribution or power transformer is energized, there occurs a short-duration inrush of magnetizing current which the transformer primary fuse must be capable of withstanding without operating (or, in the case of certain types of fuses, without sustaining damage to their fusible elements). A conservative estimate of the integrated heating effect on the primary fuse as a result of this inrush current is roughly equivalent to a current having a magnitude of 12 times the primary full-load current of the transformer for a duration of 0.1 second, and 25 times for 0.01 second. An example of the magnetizing-inrush current for a small overhead distribution transformer is shown in Figure 1. This example is from a laboratory test and is the highest inrush obtained from tests performed on this transformer. The inrush that occurs on any particular energization will depend, among other things, on the residual magnetism of the transformer core as well as the instantaneous voltage when the transformer is energized. Since these two parameters are unknown and uncontrollable, the fuse must be sized to withstand the maximum inrush that can occur under worst-case energization. The minimum-melting curve of the primary fuse should be such that the fuse will not operate as a result of this magnetizing-inrush current."
La on voit que l'appel de courant depend de la magnetization du transfo et aussi de la magnetisation residuelle!!
C'est tout Keskejedis depuis hier.
Je ne pense pas que tous gens racontent des bêtises
Maintenant si tu veux mesurer le courant d'appel d'un transfo, le mieux est une pince ampèremétrique TRMS avec detection de crete. en as tu une ?
PS: Tu aurais pu prendre un transfo de 10.000 VA ! l'exemple aurait été encore plus réaliste!
Les alim concernent l'audio, pas les machine-outils!
Euh, je m'excuse, mais un ampli de 5 voies avec 400VA par voie ça fait bien 2kVA pour moi!!
Et en plus les transfos de machine outils sont bien plus costauds que ça
Dans mon empli j'ai 1.3kVA de transfo donc mon exemple est tout sauf ridicule...
![:roll:](https://www.homecinema-fr.com/forum/images/smilies/icon_rolleyes.gif)